I just came across this from a utility's transformer standards PDF which I found rather eye opening. On page 67 it makes mention of a electrostatic charge with the secondary winding floating, which in theory makes sense considering there is a capacitive coupling between the primary and secondary windings in a typical transformer.
https://www.google.com/url?sa=t&rct...3czYWZ7aZPTLSIAEPwWoSg&bvm=bv.139782543,d.cGc
With that in mind, if secondary systems were left ungrounded, wouldn't the entire 120/240 volt secondary service be at 750 to 7000 volts potential above earth? But by grounding the secondary neutral point once at the pole and again at the main service disconnect, that induced voltage can the be "bled off", or more correctly use the earth as a return path back to POCO substation?
If that is true, then why or how does the NEC allow for an ungrounded service? :?
https://www.google.com/url?sa=t&rct...3czYWZ7aZPTLSIAEPwWoSg&bvm=bv.139782543,d.cGc
With that in mind, if secondary systems were left ungrounded, wouldn't the entire 120/240 volt secondary service be at 750 to 7000 volts potential above earth? But by grounding the secondary neutral point once at the pole and again at the main service disconnect, that induced voltage can the be "bled off", or more correctly use the earth as a return path back to POCO substation?
If that is true, then why or how does the NEC allow for an ungrounded service? :?