Maybe they needed a 90A disconnectBefore I retired I was involved in a few PV installations and admit I'm not well versed in these installations but, what would be the reason for having a 60 amp non fusible switch above a 30 amp non fusible switch.
View attachment 2569012
I just noticed that the two bottom switches each have one conduit going in the top and two coming out the bottom, all of which go to the right. It looks like they run to one of the enclosures on the opposite side of the column from what I assume is the main, but what those boxes are are anyone's guess.I would guess there are conductors that go through the top disconnect and terminate in the bottom one.
Zooming in on the photo, I don't believe that's correct; I believe each bottom switch just has one conduit exiting the bottom. The shadows and color of the concrete pillar are a bit deceptive.I just noticed that the two bottom switches each have one conduit going in the top and two coming out the bottom.
The top is connected line load, the bottom is the same. IOW's, a switch switching a switch.I would guess there are conductors that go through the top disconnect and terminate in the bottom one.
You are correct, there is one conduit with one set of wires entering the top switch which is switching a set of conductors entering the top of the lower switch which is switching a set of conductors exiting the bottom of the lower switch. There is only one circuit in each set up that routes through both top and bottom switches, a switch switching a switch.Zooming in on the photo, I don't believe that's correct; I believe each bottom switch just has one conduit exiting the bottom. The shadows and color of the concrete pillar are a bit deceptive.
I favor the speculation in post #3 that each of those conduits carries two circuits, and so you have two stacked disconnects.
Cheers, Wayne
I don't think so since one is a 60 and one is a 30.Can you switch the switches that are switching the switch?
There are actually two independent systems (modules, inverters, batteries, etc...) so for this conversation we need to ignore one set. We have one set of conductors consisting of a black and red #8. The two switches are in series from the inverter to the panel.Could you actually be getting one set just feeding through from the top one that switches the other set with second set switched on bottom one? Rather than a switch switching a switch.
Could you have actually 4 banks of PV, 2 larger banks under 60A and 2 smaller banks under 30A?
Are you speculating or did you see inside the switches?You are correct, there is one conduit with one set of wires entering the top switch which is switching a set of conductors entering the top of the lower switch which is switching a set of conductors exiting the bottom of the lower switch. There is only one circuit in each set up that routes through both top and bottom switches, a switch switching a switch.
I have been in the switches. The owner is replacing the whole set up because it was all submerged in the last Hurricane. I am helping him put a list together. The question is simply, is there any reason for two switches to be in series in any PV installation?Are you speculating or did you see inside the switches?
It certainly is.It would seem rather redundant given the proximity of the A/C disconnect and Utility disconnect