F frankgrbavcich Member Oct 21, 2008 #1 Is the wild leg of a 3 phase system identified in the 2008 code?
celtic Senior Member Location NJ Oct 21, 2008 #2 110.15 [215.8 ...'02 ~ don't know where it went in 05' & '08] 230.56 408.3(E)
Rockyd Senior Member Location Nevada Occupation Retired after 40 years as an electrician. Oct 21, 2008 #3 In at least 5 places.
Rockyd Senior Member Location Nevada Occupation Retired after 40 years as an electrician. Oct 21, 2008 #4 Beat by a Celtic by seconds...
celtic Senior Member Location NJ Oct 21, 2008 #5 I only named 3...list the other locations for bonus points!
Rockyd Senior Member Location Nevada Occupation Retired after 40 years as an electrician. Oct 21, 2008 #6 408.3(f) and 409.102