I would plug a 3 wire cord cap into a GFCI marked "No Ground Present," drill or saw or whatever. I assume the reason it is allowed to change out 2/prong receptacle to GFCI receptacle (in areas not otherwise required to have GFCI) is to make it safe to do so?
Not really. It is mostly to make it safer to plug in loads with two wire cords. The GFCI manufacturers do not make GFCI 2-wire receptacles because they could only be used for replacement of old 2-wire installed with no ground available. Not enough of a market to justify it, and too great a chance that it would be installed where it should not be.
But it could be at least marginally safer than plugging in a 3-wire cord by using an adapter that did not provide a ground either. Or it might be worse. Depends on what kind of fault you expect to happen most often:
Would you rather have the appliance frame or case floating with no GFCI protection in case of a fault or bonded to the neutral so that a fault somewhere else could energize it directly? To me that is a difficult choice to make, and one that is not necessary if you block the ground hole.