We are trying to figure out whether a 57vac input would be considered as/fall under a service entrance or feeder calculation for direct burial using USE #6 in conduit (for voltage drop). Section 300-5 exception #3 lists a feeder circuit being permitted at 12" depth with less than 15 amps and less than 300vac, which is the case for these wind units at voltage listed above. At This voltage does this even qualify as a service entrance? The unit is 3-phase AC at 57vac max. The unit than goes to a 3 pole disconnect just inside the building.