xptpcrewx
Power System Engineer
- Location
- Las Vegas, Nevada, USA
- Occupation
- Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
A two-part challenge for the electrical test technicians and/or engineers…
Consider a Δ-Y transformer with the following winding resistance measurements taken in the field:
RX1-X2: 2.667mΩ
RX2-X3: 2.672mΩ
RX3-X1: 2.645mΩ
RH1-H2: 2.428mΩ
RH2-H3: 2.315mΩ
RH3-H1: 2.445mΩ
Note: Aside from X1, X2, X3 and H1, H2, H3 terminals, all other connections are inaccessible with the X0 buried.
Question #1 (20 points): What is the value of the single lowest Y connected phase winding?
Question #2 (80 points): What is the value of the single lowest Δ connected phase winding?
Show your work or no credit.
Consider a Δ-Y transformer with the following winding resistance measurements taken in the field:
RX1-X2: 2.667mΩ
RX2-X3: 2.672mΩ
RX3-X1: 2.645mΩ
RH1-H2: 2.428mΩ
RH2-H3: 2.315mΩ
RH3-H1: 2.445mΩ
Note: Aside from X1, X2, X3 and H1, H2, H3 terminals, all other connections are inaccessible with the X0 buried.
Question #1 (20 points): What is the value of the single lowest Y connected phase winding?
Question #2 (80 points): What is the value of the single lowest Δ connected phase winding?
Show your work or no credit.