Winding Resistance Challenge

Status
Not open for further replies.

xptpcrewx

Power System Engineer
Location
Las Vegas, Nevada, USA
Occupation
Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
Once again, thanks to everyone who participated and/or contributed to this challenge, and special thanks/recognition to those who solved it. Below is my version of the solution - which is the procedure to derive the necessary equations along with the final result. In the spirit of post #13, the variables are expressed in Z = {R + jX} notation.

Note: There may be a simpler derivation than the ones shown below, but herein I have employed the "brute-force" method.

Question #1 (20 points): What is the value of the single lowest Y connected phase winding?

Let ZW1, ZW2, and ZW3 be the winding impedances connected between terminals X1-X0, X2-X0, and X3-X0 respectively.
A system of equation describing a wye circuit topology can then be expressed as:

[1] ZX1-X2 = (ZW1 + ZW2)​
[2] ZX2-X3 = (ZW2 + ZW3)​
[3] ZX3-X1 = (ZW3 + ZW1)​

Rewriting these expressions gives:

[4] ZW1 = (ZX1-X2ZW2)​
[5] ZW2 = (ZX2-X3ZW3)​
[6] ZW3 = (ZX3-X1ZW1)​

Substituting [4] into [3] yields equation [7],
Substituting [5] into [7] yields equation [8],

Substituting [5] into [1] yields equation [9],
Substituting [6] into [9] yields equation [10],

Substituting [6] into [3] yields equation [11],
Substituting [4] into [11] yields equation [12],

Rearranging expressions [8], [10], and [12] yields:

ZW3 = (1/2)·[ ZX3-X1ZX1-X2 + ZX2-X3]
ZW1 = (1/2)·[ ZX1-X2ZX2-X3 + ZX3-X1]
ZW2 = (1/2)·[ ZX2-X3ZX3-X1 + ZX1-X2]

Plugging in RX1-X2 = 2.667·mΩ, RX2-X3 = 2.672·mΩ, RX3-X1 = 2.645·mΩ into the above equations gives:

ZW1 = 1.320·mΩ
ZW2 = 1.347·mΩ​
ZW3 = 1.325·mΩ​

Hence by inspection, Winding 1 is the single lowest Y connected phase winding.

Question #2 (80 points): What is the value of the single lowest Δ connected phase winding?

Let ZW1, ZW2, and ZW3 be the winding impedances connected between terminals H1-H2, H2-H3, and H3-H1 respectively.
A system of equation describing a delta circuit topology can then be expressed as:

[1] ZH1-H2 = [ZW1 || (ZW3 + ZW2)] = {[ZW1·(ZW3 + ZW2)]/[ZW1 + (ZW3 + ZW2)]}​
[2] ZH2-H3 = [ZW2 || (ZW1 + ZW3)] = {[ZW2·(ZW1 + ZW3)]/[ZW2 + (ZW1 + ZW3)]}​
[3] ZH3-H1 = [ZW3 || (ZW2 + ZW1)] = {[ZW3·(ZW2 + ZW1)]/[ZW3 + (ZW2 + ZW1)]}​

Subtracting [1] and [2] yields equation [4],
Subtracting [2] and [3] yields equation [5],
Subtracting [3] and [1] yields equation [6],

Adding [4] and [3] yields equation [7],
Adding [5] and [1] yields equation [8],
Adding [6] and [2] yields equation [9],

Dividing [7] by [8] yields equation [10],
Dividing [8] by [9] yields equation [11],
Dividing [9] by [7] yields equation [12],

Substituting [10] and [11] into [7] yields equation [13],
Substituting [10] into [13] yields equation [14],

Substituting [11] and [12] into [8] yields equation [15],
Substituting [11] into [15] yields equation [16],

Substituting [12] and [10] into [9] yields equation [17],
Substituting [12] into [17] yields equation [18],

Rearranging/simplifying expressions [14], [16], and [18] yields:

ZW2 = {ZH2-H3 + (1/2)·[(ZH3-H1ZH1-H2 + ZH2-H3)·(ZH2-H3ZH3-H1 + ZH1-H2)]/(ZH1-H2ZH2-H3 + ZH3-H1)}
ZW3 = {ZH3-H1 + (1/2)·[(ZH3-H1ZH1-H2 + ZH2-H3)·(ZH1-H2ZH2-H3 + ZH3-H1)]/(ZH2-H3ZH3-H1 + ZH1-H2)}
ZW1 = {ZH1-H2 + (1/2)·[(ZH1-H2ZH2-H3 + ZH3-H1)·(ZH2-H3ZH3-H1 + ZH1-H2)]/(ZH3-H1 ZH1-H2 + ZH2-H3)}

Plugging in RH1-H2 = 2.428·mΩ, RH2-H3 = 2.315·mΩ, RH3-H1 = 2.445·mΩ into the above equations gives:

ZW1 = 3.688·mΩ
ZW2 = 3.363·mΩ
ZW3 = 3.743·mΩ​
Hence by inspection, Winding 2 is the single lowest Δ connected phase winding.
 