What is the ampere rating of: 1.5mm2, 2.5mm2, and 4mm2 pvc insulated copper conductor? Please forgive the elementary question, but the machine in question is a German import with these wire sizes.
 
I am going to say that without providing the temperature you are willing to run the conductor at you can not determine the ampacity of a conductor.

A 14 AWG might carry 150 amps if you are willing to run it that hot.

Comparing relative sizes from the NEC might get you in the same ball park but is still just a guess.
 
I found this IEC calculator for sizing conductors, but I do not which parameters to enter.

Where is Bes?


Bes would help.:D I posted over on a UK ET forum and already a guy is telling me to visit the American forums:lol::blink::rant: The others are helping but are looking at me like a space alien. :p
 