wire ampacity
lesh
what is the ampacity of 8-500kcm wires in open raceway feeding a 3000 amp breaker.
at 480y/277.
Define an open raceway? What type of insulation? Conductor material? As Bob said more info is required.
Is it 8 wires per phase?
Is it CU or AL?
What is an open raceway?
What is the termination temp?
What insulation is on the wire?
3040A is a fair guess. If we had all the information, we could dial down tight.
Off the cuff with ALOT of assumptions made to fill in the gaps (see specific questions in other posts) the amperage would be 3040 amps. This assume copper THHN condutors, 75 degree terminations and a "typical" parralell installation. I do not know what an "open" raceway is so this may or may not factor into the answer.
. . . feeding a 3000 amp breaker at 480y/277.
These two tidbits have no impact on ampacity. Why are you asking this question? Is is some kind of homework assignment, or is this related to an actual installation?
8 wires per phase
cu wire
cable tray with cover
75 ?
THHN
according to Nec 2008 art 310.16 its 380amps , but I have more than 3 current carrying conductors. Also table 310.15 (B) (2) (a) adjustment factors for more than 3 conductor.
confused by code?
Is it 8 wires per phase? 8
Is it CU or AL? cu
What is an open raceway? cable tray with cover
What is the termination temp? 75
thhn
I want to figure out per nec 2008, I am a little confused by art 310.16 about 3 current carrying conductor, per this existing installtion there is 8. What would be the correct ampacity, 380a ?
No its not home work, I want to make sure that the existing installation wire ampacity is correct for the breaker, a maintenace super. said the installation , years ago was not to its proper ampacity, According to nec 2008 art. 310.16, the ampacity could be 380amps. But this installtion has more than 3 current carrying conductors.
Within the context of the NEC, cable trays are not raceways.
For cable 0-2000V, the ampacity is calculated per Section 392.11. In general, 310.15(B)(2)(a) will only apply to multi-conductor cables with four or more current carrying conductors.
Beyond the factors you have already clarified, the conductor layout within the tray, the tray?s ventilation method (if any) and whether the cables are single or multi conductor are also relevant. As always, ambient temperature is also relevant.
Cable layout is often a critical issue and easily overlooked. Section 392.11 assumes the conductors are installed per Sections 392.9 or 392.10, whichever is appropriate.