A friend asked me to size the wire and breaker for a geothermal heat pump. Here are the specs:
240V, 1 phase; 27.7 Full Load Amps; Min. circuit ampacity 32.2 Amps; Max. HACR breaker 50 Amps.
Can he install a 50 amp HACR breaker and run #8 wire (40 Amps at 60 deg.), or is #6 wire required (55 amps at 60 deg.) for a 50A breaker?
Steve