I would like your opinion on this. We have been working on a subdivision entrance way lighting
project. The lights are 120V 6AMP total. The circuit is protected by a GFI breaker. The
disagreement starts in 300-5. The AHJ says this wire must be 18in. deep. I told him it
should be under 300-5 column 4.(residential branch circuit). He said it's not residential.
I asked him " What is the classification". He said " It's a common area." After this I called NEC public affairs. They initially agreed with AHJ, but upon closer review said this circuit
is under 300-5 column 4. What do you guys think
of this?