So you would derate the field wires but not the original wires based on the total number of CCCs when you are finished?
I don't think you have any choice.
So you would derate the field wires but not the original wires based on the total number of CCCs when you are finished?
I agree, but with the proviso that if it is not clear that the panel builder intended for field wiring to be added to the Panduit, I would not feel safe in ignoring any possible derating of the original wiring.I don't think you have any choice.
I don't agree. The NEC applies to the field wiring in the panel. That wiring is not subject to the rules that applied to the construction of the panel. The field wiring is subject to the rules in the NEC.
I agree, but with the proviso that if it is not clear that the panel builder intended for field wiring to be added to the Panduit, I would not feel safe in ignoring any possible derating of the original wiring.
Just because there is no fill requirement does not mean that the current carrying conductors do not produce heat. It is my opinion, that the derating rules apply to the field installed conductors in the panel any time that the conductors are installed without maintaining spacing between the conductors. Also the derating rules are really wire sizing rules.But the NEC doesn't specify fills for panduit and other wireways commonly used in control panels.
For me, I just make sure my wires/cables are sized right per NEC and run it into the panel. The NEC rules don't exist
for the raceway fills in the box, so how can they apply to anything other than wire sizing in this case?
But the NEC doesn't specify fills for panduit and other wireways commonly used in control panels.
For me, I just make sure my wires/cables are sized right per NEC and run it into the panel. The NEC rules don't exist
for the raceway fills in the box, so how can they apply to anything other than wire sizing in this case?
310.15(B)(3) Adjustment Factors.
(a) More Than Three Current-Carrying Conductors in a
Raceway or Cable. Where the number of current-carrying
conductors in a raceway or cable exceeds three, or where
single conductors or multiconductor cables are installed
without maintaining spacing for a continuous length longer
than 600 mm (24 in.) and are not installed in raceways, the
allowable ampacity of each conductor shall be reduced as
shown in Table 310.15(B)(3)(a). Each current-carrying con-
ductor of a paralleled set of conductors shall be counted as
a current-carrying conductor
But the NEC doesn't specify fills for panduit and other wireways commonly used in control panels.
For me, I just make sure my wires/cables are sized right per NEC and run it into the panel. The NEC rules don't exist
for the raceway fills in the box, so how can they apply to anything other than wire sizing in this case?
310.15(A)(2) Selection of Ampacity. Where more than one ampacity
applies for a given circuit length, the lowest value shall be
used.
Exception: Where two different ampacities apply to adjacent
portions of a circuit, the higher ampacity shall be permitted to
be used beyond the point of transition, a distance equal to 3.0
m (10 ft) or 10 percent of the circuit length figured at the
higher ampacity, whichever is less.