I am considering a modification to the values in table 310.15( C )( 1 ), Adjustment Factors for more than 3 Current Carrying Conductors. This is for a specific application only. In this forum I am looking for feedback to point out any flaws in my thinking.
What is the maximum number of # 12 awg, cu, conductors that I can run in a raceway with each ungrounded conductor protected at 20 amps.
Using table 310.16, 90 deg C column, #12 awg, THWN-2 wire is good for 30 amps. Using table 10.15( C )( 1 ) I can use 9 wires (30 amps x 70 percent = 21 amps.
Table 310.15( C )( 1 ), is based on each wire being fully loaded. This is mentioned in the handbook notes following this table. However, in my application all conductors have been selected for 80 percent load.
If I have 9 #12 awg, 20 amp circuits loaded at 20 amps, and my wire resistance is 2 ohms per thousand feet from table 9 in the annexes, this arrangement will generate 7200 watts per thousand feet. 9 x 20A x 20A x 2.0 ohms/1000 feet.
If my wire is only loaded to 80 percent, the amount of heat generated per wire is 16A x 16A x 2 ohms/1000 feet = 512 watts.
The number of 80 percent wires needed to generate 7200 watts is 7200/512 =14.
My conclusion is that I can run 14 #12awg wires in a common raceway.
Issues that I have not considered but could effect my conclusion, increasing the number of wires.
1. I have not considered an ambient temperature adjustment.
2. the 2 ohm/1000 feet value I believe is the worst case condition and the actual value may be less.
3. If going from 9 to 14 wires requires a larger conduit this will make my calculation more conservative.
Thank you for your comments
What is the maximum number of # 12 awg, cu, conductors that I can run in a raceway with each ungrounded conductor protected at 20 amps.
Using table 310.16, 90 deg C column, #12 awg, THWN-2 wire is good for 30 amps. Using table 10.15( C )( 1 ) I can use 9 wires (30 amps x 70 percent = 21 amps.
Table 310.15( C )( 1 ), is based on each wire being fully loaded. This is mentioned in the handbook notes following this table. However, in my application all conductors have been selected for 80 percent load.
If I have 9 #12 awg, 20 amp circuits loaded at 20 amps, and my wire resistance is 2 ohms per thousand feet from table 9 in the annexes, this arrangement will generate 7200 watts per thousand feet. 9 x 20A x 20A x 2.0 ohms/1000 feet.
If my wire is only loaded to 80 percent, the amount of heat generated per wire is 16A x 16A x 2 ohms/1000 feet = 512 watts.
The number of 80 percent wires needed to generate 7200 watts is 7200/512 =14.
My conclusion is that I can run 14 #12awg wires in a common raceway.
Issues that I have not considered but could effect my conclusion, increasing the number of wires.
1. I have not considered an ambient temperature adjustment.
2. the 2 ohm/1000 feet value I believe is the worst case condition and the actual value may be less.
3. If going from 9 to 14 wires requires a larger conduit this will make my calculation more conservative.
Thank you for your comments