wdalrymple
Member
I found the situation,created by an electrical contractor, listed below and need some input on what they can do to fix the problem.
1 100 amp panel with 2 2" conduits 5' in leangth, 1 has 17 current carrying conductors
the other has 18 current carrying conductors.
they are on 20 amp breakers.
this makes the ampacity of each wire 12.5 amps
can you by code attach a 20 amp duplex receptacle to this conductor.
to fix this they can add more conduit?"how many"?
or they can increase the wire size "how much"?
each circuit runs to 2 gfi's in the bathroom and 2 other receptacles in the dorm rooms" total 4 duplex receptacles"
this is work that is still withen the 12 month warrenty period.
thanks for your input and ideas
Will Dalrymple
1 100 amp panel with 2 2" conduits 5' in leangth, 1 has 17 current carrying conductors
the other has 18 current carrying conductors.
they are on 20 amp breakers.
this makes the ampacity of each wire 12.5 amps
can you by code attach a 20 amp duplex receptacle to this conductor.
to fix this they can add more conduit?"how many"?
or they can increase the wire size "how much"?
each circuit runs to 2 gfi's in the bathroom and 2 other receptacles in the dorm rooms" total 4 duplex receptacles"
this is work that is still withen the 12 month warrenty period.
thanks for your input and ideas
Will Dalrymple