I have a question on conductor sizing. I am using table 400.5(B) and a G-GC Type cable. My load is 104.2A and is all non-continuous. I also have 4 current carrying conductors with a 4wire+gnd cable.
1) Do I only have to derate for the extra current-carrying conductor for 90degC using the .8 factor?
2) Or do I still have to use have to derate from the 75degC for the extra current-carrying conductor?
I am trying to get down to use a #2 cable. 0.8*152=121.6A from 90degC column and 0.8*133=106.4A. Is this restricted by table 310.16 for 115A?
Just trying to get my numbers.