Installing a 1200A 480v 3ph service, feeder conduits tie into a ct cabinet first, then into the MDP, due to the layout of the mechanical room and the size of the cabinets and the location of the main 1200A breaker in the MDP, I want to feed the MDP from the ct cabinet with a trough. There will be 4 sets of 350mcm (16 wires). May I use a trough and if so how do I size it?
 
366.22 is a good place to start.
Then go to table 5 in the back of the book to find your conductor size. (.5242)
multiply .5242x16=8.3872 that will be the 20% allowed by 366.22
8.3872x5=41.936 sq inches. the square root of 41.936 is 6.4758011.
You need a trough bigger than 6x6.