I do service work for a large grocery store chain. I got a call today where they said an outlet wasn't working. I get there and when I see it in the bakery, I realize exactly what the problem is, as this is the 4th time I've seen it. When they did the slab work, the installing electricians are running the conduit underneath the ovens. The pipes still get water in them and then you add the head from these large ovens, it cooks the THHN wire. In that, I mean it comes out bubbled and white.
Since this is a problem and replacing the wire with THHN again will result in the same problem down the road, I'm wondering what else out there may work. I'm leaning towards XHHW-2. Does anybody have any thoughts on this, or maybe have dealt with something similar. I need something to withstand the higher temp, and be water resistant.
There is always the option of re-piping this, but that's a last resort because of the distance and expense.
Thoughts?
Since this is a problem and replacing the wire with THHN again will result in the same problem down the road, I'm wondering what else out there may work. I'm leaning towards XHHW-2. Does anybody have any thoughts on this, or maybe have dealt with something similar. I need something to withstand the higher temp, and be water resistant.