Greetings!
I Have a project where we designed the replacement of all existing panels installed in a middle school (circa 1965). Scope of work is to disconnect and remove existing panel & panel feeder, retain existing panel feeder raceway for installation of a new panel feeder. Install new panel in existing location, install new feeder in existing conduit (conduit size was confirmed acceptable for new feeder) and reconnect all existing branch circuits to new circuit breakers.
Drawings were reviewed and approved by a third party reviewing agent for permits. Now local inspector is indicating that the since the existing wiring in the building only used 60-degree insulation he wants every existing circuit from termination @ panel to nearest junction point or device to be replaced with wiring with 90-degree insulation. Not the entire circuit, just the portion of the circuit which terminates on the new panel.
I started investigating this so I thought I would put it out the on the forum to get some other opinions. I thought terminating wiring with 60-degree insulation on lugs rated for 75-degree wire is acceptable. Keep in mind all circuits are rated 100A and under (majority are 20A circuits)
Article 110.14 (C)
The temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor or device.
This inspector seems to think the temperature rating of the conductor’s insulation must meet or exceed the temperature rating of the termination.
Am I missing something here? I did not receive shop drawings from the contractor but assume the lugs on the new panels are rated for 75-degree wire as most are only rated for this.
Thank you in advance for your response.
I Have a project where we designed the replacement of all existing panels installed in a middle school (circa 1965). Scope of work is to disconnect and remove existing panel & panel feeder, retain existing panel feeder raceway for installation of a new panel feeder. Install new panel in existing location, install new feeder in existing conduit (conduit size was confirmed acceptable for new feeder) and reconnect all existing branch circuits to new circuit breakers.
Drawings were reviewed and approved by a third party reviewing agent for permits. Now local inspector is indicating that the since the existing wiring in the building only used 60-degree insulation he wants every existing circuit from termination @ panel to nearest junction point or device to be replaced with wiring with 90-degree insulation. Not the entire circuit, just the portion of the circuit which terminates on the new panel.
I started investigating this so I thought I would put it out the on the forum to get some other opinions. I thought terminating wiring with 60-degree insulation on lugs rated for 75-degree wire is acceptable. Keep in mind all circuits are rated 100A and under (majority are 20A circuits)
Article 110.14 (C)
The temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor or device.
This inspector seems to think the temperature rating of the conductor’s insulation must meet or exceed the temperature rating of the termination.
Am I missing something here? I did not receive shop drawings from the contractor but assume the lugs on the new panels are rated for 75-degree wire as most are only rated for this.
Thank you in advance for your response.