This spec section is a bit confusing. Wires in conduit(IMO) would NOT be USE. What insualtion do you think they are referring to for wires in conduit in this situation?
Cables for incoming service, or wire in conduits
contiguous with the earth, in concrete, or other damp or wet locations, must be synthetic rubber insulated
with neoprene jacket, heat and moisture resistant and must be equal to UL Type USE and rated for 600
volts at 75 degrees C. for both wet and dry locations.