I have a 800a 480v 3p MDP in a boiler room that feeds about 200 feet to a penthouse for hvac equipment. The wires are 500kcmil type TW 60degC in parallel, for a total of 640amps. 3 in each pipe. I don't want to replace the wires but the loads are one small pump moter that uses 20 amp ocpd ,and two rtu's that have a marked MCA of 338a. The total is now 696a.I don't think you can do this but i thought i would ask, can i use 240-3 to use 700a fuses to supply this and be legal?thanks, john