I guess I should have not disagreed. I should have asked the question.
Bob, thanks for clearing that up for me (310.13). I should have asked the supplier to send MTW 60c. I always just asked for MTW. I would get 90c wire that is not the wire of my choice for panel building. The thermoplastic coating is the difference I assume. I did not know that the wire I wanted was rated at 60c.
dlhoule,
Wire size depends on the control circuit load. When building motor control panels you sometimes have NEMA 5 size contactors. The coil in this contactor or contactors can consume a good bit of current. It just depends on the load.
MTW at 60c is larger in diameter (insulation) than MTW 90c. The thermoplastic coating on the 90c wire is much more slick than the 60c wire. That is why I would not want to be pulling it in conduit, and I don't think it is intended for that purpose. But that does not mean you can't. Personal preference.
Bob, thanks for clearing that up for me (310.13). I should have asked the supplier to send MTW 60c. I always just asked for MTW. I would get 90c wire that is not the wire of my choice for panel building. The thermoplastic coating is the difference I assume. I did not know that the wire I wanted was rated at 60c.
dlhoule,
Wire size depends on the control circuit load. When building motor control panels you sometimes have NEMA 5 size contactors. The coil in this contactor or contactors can consume a good bit of current. It just depends on the load.
MTW at 60c is larger in diameter (insulation) than MTW 90c. The thermoplastic coating on the 90c wire is much more slick than the 60c wire. That is why I would not want to be pulling it in conduit, and I don't think it is intended for that purpose. But that does not mean you can't. Personal preference.