jwelectric
- North Carolina
Al my point being that it is not dot 10 of either article mentioned in this thread that prohibits the installation of wire molding in a damp or wet location.
380.10 uses Permitted. The use of a multioutlet assembly shall be permitted in dry locations.
384.10 Uses Permitted. The use of strut-type channel raceways shall be permitted in the following: (1) Where exposed. (2) In dry locations.
386.10 Uses Permitted. The use of surface metal raceways shall be permitted in the following: (1) In dry locations.
All three of the dot 10s are permissive rules and do not prohibit anything.
90.5(B) Permissive Rules. Permissive rules of this Code are those that identify actions that are allowed but not required, are normally used to describe options or alternative methods, and are characterized by the use of the terms shall be permitted or shall not be required.
It?s neither of these articles that prohibit the installation but the listing of the raceway that prohibits the installation which as you point out would be a violation of 110.3(B): Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
Take notice that each post I was addressing the dot 10 section and then asking the question ?where? is it prohibited.
Thank you for posting the insert.