I believe they are 600 volts. They are not rated in amps just volts.rjh1 said:Im wondering if someone can help resolve a wire nut question. What voltage and amperage are tan twister wire nuts good for?
rjh1 said:I guess Im asking, is it correct by saying whatever the wire is rated for that you are twisting together, Thats what the wire nut is good for?
rjh1 said:So If i took a 40 amp feed (#8s) to a motor and tie on to # 10 at the motor, this would be ok?
iwire said:If I was going the wire nut route for that connection I would use an Ideal 454 blue.
76nemo said::-? Who's twisting???? 17 drives????
ZZZ said:The wire nuts in the motor j-boxes were preexisting and not disturbed until they started failing.
MichaelGP3 said:How exactly did they fail? Melt? Metal spring corrode? Loosen by themselves? Some VFD's use the Buchannan 500 series European style terminal blocks for field connections; I've not yet heard of a failure when using these.....
rjh1 said:So If i took a 40 amp feed (#8s) to a motor and tie on to # 10 at the motor, this would be ok?
twoelk said:If this were me, I would not use wirenuts to terminate these, I would use the bolt and tape method.
bolt and tape is old school. i dont mind doing it that way at all. but polaris or ilsco connectors of the same design are easier and faster. either way works just as well. i still show my helpers how to make up burndys with rubber tape and electrical tape even with the invention of the insulated tap connectorpeter d said:Bolt and tape? Yuck...Use some "polaris" style connectors instead.
electricalperson said:bolt and tape is old school. i dont mind doing it that way at all. but polaris or ilsco connectors of the same design are easier and faster. either way works just as well. i still show my helpers how to make up burndys with rubber tape and electrical tape even with the invention of the insulated tap connector
rustyryan34 said:What do you mean by "burndys" i have never heard that before?