KarlD
Member
- Location
- Pennsylvania
- Occupation
- not an electrician
Hi All - I am having a contractor install a new heat pump system with a label that shows a 40A recommended breaker size, and 30.5A MCA. They are running the circuit with 10 gauge wire. I have always thought of 10ga as having a 30A max. Does this meet code in this application, or should they be upsizing to 8ga? Thanks in advance for your advice.