ivol
New member
- Wilmington, MA
I'm working on upcoming project where I need to delivery 3200 Amps / 8 VAC from Scott T transformer to my filament. What size of wire I should use?
Thanks
Thanks
The transformers are essentially wound with busbar to get that level of current.3200 amps at 8 volts? Are you sure that's correct?
I don't know anything about scott transfomers, or whatever your application is, but say you start with 16 volts, you can have a maximum resistance of .0025 ohms to still have 8 volts left at your filament.
At that current I'd keep the distances short and use copper busbars.I'm working on upcoming project where I need to delivery 3200 Amps / 8 VAC from Scott T transformer to my filament. What size of wire I should use?
Thanks
It is in the caculations/engineering forum and not the NEC forum. Still seems pretty strange to run such a low voltage at such a high current.Scott T transformers are for supplying 2 phase power... what on Earth are you working on that would require 3200A @ 8VAC of 2 phase power? Looks like a vacuum tube heater, and something isnt right with your numbers. Regardless, I doubt this is an NEC question or installation.... 2016 code cycle.... yeah....
3200 amp @ 8 volts = 25.6 kVA. If it is two phase probably need double that to 51.2 kVA.
Put 51.2kVA on 480 volt three phase and you only draw 61.5 amps and spend a lot less on conductors. Has to be a very special reason to need to run at 8 volts.
As mentioned earlier, FWIW, two equal heaters in quadrature on two phase or a corner fed square on two phase produces a uniform total heat input over time. Three phase would take three heaters to achieve the same result.Fairly common for glass furnace electrodes
2 phase with corner placement is a std arrangement