Well, that depends on your definition of "ever."If that ever happened the NEC would not allow this rule.
Well, that depends on your definition of "ever."If that ever happened the NEC would not allow this rule.
That's silly. If you truly understand why it is okay to wire an a/c with a smaller wire than the OCPD, then you wouldn't worry about the building burning down. If that ever happened the NEC would not allow this rule.
Unless the highway patrol has a building in Angola you're safe! :grin:
It most likely wouldn't but when the building could be hundreds of mile away from where it was manufactured and people are pointing fingers we don't want them pointing at us. We've actually had customers call us and want to know how we could install an A/C unit with undersized wires from the factory in them!
Example: MCA is 60. We found a wire from the factory that couldn't have been much bigger than a #10! That must be why the compressor failed! We're not paying for this!
Then we have to explain we have no control over what the factory uses and it is all legal because it has a UL label on it.
It just ain't worth it......
The "Mnimum Circuit Ampacity" is 17. The ampacity of #12 THHN is 25, and that exceeds the minimum. Yes, you can use #12.