D_Norris
New member
- Location
- Baltimore, Maryland, United States
My company installed LED lights in a school. The branch circuit is a 20 amp breaker with 12-2 wire. We installed 40 watt LED panels and a ceiling sensor with 14-3 MC from the switch leg box. The inspector failed us do to the fact the breaker is 20 amp therefore all wire must be 12 gauge. The ceiling sensor only draws 3 amps and has 18 wire hooked up internally. I referenced 240.5 (B)(2) witch states 14 can be used as fixture wire on a 20 amp breaker, but also went to table 402.3 and THWN is no listed. Is there any other code I should reference?
Thanks all
Thanks all