Sorry XHHW-2 90 degree. The lugs are rated for 90How are you getting 4/0 al and #2 al for 200A and 100A feeders?
Sorry XHHW-2 90 degree. The lugs are rated for 90How are you getting 4/0 al and #2 al for 200A and 100A feeders?
I agree if a 200 ampere breaker is on the line side of the cable while fed from 3 x larger 500 kcmile wires its not a tap.There are no taps in your illustration therefore the taps rules do not apply. There should not be a ground in the 4".
View attachment 2575476
Egc needed to bond everything metalWhy should there not be a ground? this is coming from a piece of switchgear, not a new service.
The pic shows service terminatinr into a 200 ampere breaker neat j box. A breaker upstream of tap doesnt make a tapDisregard my initial response. When I saw the pole I thought that these were service conductors and they're actually a feeder.
It depends where the 500 kcmil in and 4/0 out is taking place. Is the 100 fused disconnect upstream on the line side of the smaller 4/0 run? If so its not a tap. If not its a tapThe pic shows service terminatinr into a 200 ampere breaker neat j box. A breaker upstream of tap doesnt make a tap
You can't use the 90 degree collum to size conductors even if the lugs are rated 90. You can next size up a 4/0 AL to 200, but a #2 is 90 which is a standard size so no higher.Sorry XHHW-2 90 degree. The lugs are rated for 90