Wire Size Using Tap Rule

There are no taps in your illustration therefore the taps rules do not apply. There should not be a ground in the 4".

View attachment 2575476
I agree if a 200 ampere breaker is on the line side of the cable while fed from 3 x larger 500 kcmile wires its not a tap.

Im not sure if this is what you meant but a tap has no protection for the smaller wire at its line side other than a breaker for the larger wire it connects to at the line side. Tap terminates at OCP for overload protection at its load side of wire
 
Disregard my initial response. When I saw the pole I thought that these were service conductors and they're actually a feeder.
The pic shows service terminatinr into a 200 ampere breaker neat j box. A breaker upstream of tap doesnt make a tap
 
I guess
The pic shows service terminatinr into a 200 ampere breaker neat j box. A breaker upstream of tap doesnt make a tap
It depends where the 500 kcmil in and 4/0 out is taking place. Is the 100 fused disconnect upstream on the line side of the smaller 4/0 run? If so its not a tap. If not its a tap
 
Forget the word 'service'. This is a feeder.

There is a 300A breaker supplying a long run of conductor to a distribution block, and then short runs of conductor from the block to 100A and 200A disconnects.

The short conductor runs are less than 300A ampacity. They are taps.

Jonathan
 
In particular see:

If you actually have equipment where _everything_ has been rated for 90C (not just the lugs), then you can use the 90C ampacity. According to the above document no such equipment is available.

-Jonathan
 