jyohnyb
- wilmington nc
If i have a main panel with six throws of the hand but no main breaker what do i size the wire on? Say it has a 100 amp to a subpanel and a 125 amp to the heats. Do i use 125% of largest breaker?
They are using the 6 throws of the hand rule. Its a 3/0 copper from the meter to the lugs. Then it is a 125 amp breaker to a heat subpanel and a 100 amp breaker to the house subpanel.
3/0 copper is good for 200 amps. However you have a total of 225 with the 2 breakers. How do i size the feeder
In many residential services, especially in San Antonio, even in new construction, there is no OCPD ahead of the MLO panel. It seemed strange to me the first time I saw it, but now I have seen lots of them.There is no OCP ahead of the MLO?