Wire size
Therealcrt
Kansas City
A single phase 120/240v 60amp panel.
The source is 300ft away it’s just a temporary panel serving a contractors trailer. Using aluminum wire wouldn’t it be 2/0 with #4 ground? That’s a voltage drop of 5%
My calculator comes up with a #2 AL for 5% if you use the full 60 amp load.
(I image the actual load is far less )
Aluminum correct? #4 copper for 60amp which is #2 for standard length but with the 300ft shouldn’t it be atleast 1/0??
What current value are you using for the calculation? Personally for a temp feeder I would not be very concerned with VD.
True. I’m using 60a it’s just a long run if I use #2 aluminum the voltage would be around 108v
Just going off the VD calc results other have posted, that's correct for the completely unbalanced case of 0A on L1, 60A on N and L2. But that case isn't very likely.
If you are willing to restrict the design cases to up to 60A on L1 / L2, and an unbalance of at most 30A (N = L1-L2 <= 30A), then your L-N voltage will be at least 114V.
Cheers, Wayne