Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
The FLA is irrelevant for sizing the conductors. The FLC from Table 430.250 times 125% will give you the minimum conductor size.As an example circuit #11 HWP-104. the FLA is 77 amps but the fuse is 150A. So the OCPD(150a Fuse) wire needs to be sized to at least 150A? I am a little confused because the FLA is 77A. I guess your also need to add 125% to the 77A?
View attachment 2580633