One set of 1500 Kcmil copper in 5" RMC would do it.Originally posted by tdjs:
What size of wire/conduit do you need for a 600 amp single phase-120/240 overhead service?
You must be talking about EMT?Originally posted by don_resqcapt19:
6 XHHW-2 400kcmil in one 3"
Don, for an OH service, wouldn't you probably use RMC? Per Table C.8, the max. # in 3" is 5 conductors for XHHW-2. You would need 3-1/2" if you used RMC. Same deal if you use IMC.Originally posted by don_resqcapt19:
6 XHHW-2 400kcmil in one 3"
Bob, IF this was for a dwelling service entrance, could you use Table 310-15(B)(6) wire ratings? Are you prohibited from using these ratings if you parallel the conductors?Originally posted by iwire:
I might go with two sets of 350 Kcmil copper in two 3" RMCs.