wire size
Re: wire size
Originally posted by tdjs:
What size of wire/conduit do you need for a 600 amp single phase-120/240 overhead service?
One set of 1500 Kcmil copper in 5" RMC would do it. ;)
I might go with two sets of 350 Kcmil copper in two 3" RMCs.
Re: wire size
Originally posted by don_resqcapt19:
6 XHHW-2 400kcmil in one 3"
Don, for an OH service, wouldn't you probably use RMC? Per Table C.8, the max. # in 3" is 5 conductors for XHHW-2. You would need 3-1/2" if you used RMC. Same deal if you use IMC.
If you could use EMT, you could get by with 3". Per Table C.1, you can put 6 #400 XHHW-2 (or 6 #400 THHN) into 3" EMT.
Question: Why did you choose XHHW-2 over THHN? Both are rated 380A at 90 degrees.
You would have to derate either to 80% = 380X.80= 304A/wire, right?
Edited to add: Bob beat me to it while I was typing my reply and raiding the fridge!
[ September 24, 2005, 01:39 PM: Message edited by: tx2step ]
Re: wire size
Bob, IF this was for a dwelling service entrance, could you use Table 310-15(B)(6) wire ratings? Are you prohibited from using these ratings if you parallel the conductors?
For a dwelling, could you use 2 sets of #250 Cu THHN, each set in 2" RMC?
Re: wire size
2step in my opinion Table 310.15(B)(6) can not be used to parallel conductors.
That table is not an ampacity chart, part of the text that goes with it says "For dwelling units, conductors, as listed in Table 310.15(B)(6), shall be permitted as".
I take 'as listed' to mean we can only use that table if we follow the table exactly.