wire size

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
The electrician you hire should know.

You question can not be answered with the info given.

What is the calculated load?

Copper or Aluminum conductors?

Steel, Aluminum, PVC conduit or direct buried?

Parallel conductors or single?

Are the conductors covered by the NEC or the NESC?

How much voltage drop are you willing to live with?

Does your area have voltage drop limitations?

Are there large motor loads?

What voltage?

Single or 3 phase?
 