Wanted to challenge the sizing of wire am I correct that the 3/0 to the 400amp is to small or am I missing something? TIA


Never mind its two 3/0 conduits I missed that right after post of course
 

Attachments

  • Scan_Doc0002.jpg
    Scan_Doc0002.jpg
    122.2 KB · Views: 0
The two sets of #3/0's is fine for 400 amps. You could use a #4 Cu in each raceway instead of the #3.
 