Tom I hear you but in many areas the power company will not hook up if it is not done to their standards. I have heard many cases were the power company oversteps their ground.
In this case if they say it is okay and the nec say it isn't then IMO you must do it as the nec states. In some states the power company decides things they have no business looking at. Some will not allow just a ufer but want 2 rods also....
Dennis
That just blows my mind! Requiring 2 driven rods as a supplement to an Ufer Ground is moronic. I have ground impedance tested a lot of installed Ground Rods and Ground Rod Arrays; including the notorious 2 rods 6 feet apart; and when I got down to less than 25 OHMS I considered myself blessed. I've seldom had a Concrete Encased Electrode come in above ~10 OHMS except when the concrete contractor forgot to stub up an actually tied piece of Rebar and had shoved a spare scrap of rod in during the pour to try and get over. The clue was that the stub was not plumb. There was no way a fully tied piece of rebar was going to get 20+ degrees out of plumb.
I told the concrete contractor right to his face that I didn't believe it was actually installed and he threatened me. I turned to the GC's Site Superintendent and said "Utterance Of Threat." He already new that he had to ban the man from the site or the Bull Steward would have all of the unionized workers drag up and idle the job. He was banned with over half of the 200 foundations not yet poured. He had to hire someone to supervise the work because the Bull Steward would not relent on the threat ban. I put my head together with the Electrical Inspector and his chief with hat in hand humility and found out that none of the 70+ pours had ever been called for inspection. The Code enforcement guys were good to me and excepted Ground Rings as substitutes. With none of the foundations yet back filled it didn't even cost the GC a lot of money and I didn't mind groveling in order to get the situation back under control in the regulatory relations department.
Funny thing the supply house sold me quite a few cut lengths of 2/0 Copper at the scrap price which I used in place of the minimum size of #2 AWG. I didn't even ask how they happened to come into having those hanging around. All but a couple of them were more than long enough to go completely around the footers with enough left to reach the Service panel. One buriable high pressure crimp connector per house and we were good to go.
Therein lies a question. I the crimped the Ground Ring Conductor back to itself were it came back to the Service Equipment on those houses because it seemed like a good idea but does the NEC actually require that? I'm really starting to dislike being so out of touch with current practice and having forgotten NEC stuff that I used to know from memory! The superintendent for my employer had no reason to question the cost because the Ground Rings were an extra for us. I'll just go ahead and admit that superintendents and project managers have had to curb some excesses that I came up with a few times over 40 + years although it was not anything like a frequent thing.
At least once I turned out to be right after being told that using 4/0 Aluminum to each of 2 200 Ampere panels which made up the service for one home was perfectly OK. I was arguing that the code didn't allow us to use the exception for service conductors when sizing feeders unless it was THE supply to the entire dwelling. You older guys and gals will remember that the exception was not terribly clear when the McMansion era began and double 200 amp panels became pretty routine. I know that a lot of those split loads were wired under the exception table before the NFPA code committee made the language clearer that it could only apply to a single set of service or feeder conductors for each home. The inspector did make us replace it with the full size calculated for the load. The superintendent thought I had asked the inspector to do it just to win the argument but when I pointed out I had been in hospital for a fire service injury for that inspection and had not even met that inspector yet he apologized.
--
Tom Horne