Noooorm
Member
- Location
- Henderson, CO
I'm working on a project for the US Government in Afghanistan. The project is supposed to be designed per the NEC. I sized the wiring from distribution panels to buildings per the feeder breaker sizes, taking into account the appropriate derating factors for temperature and number of current carrying conductors. Up to 100A, I derated from the 75 deg C column, and over 100A I derated from the 90 deg C column (Table 310.16). Then I found out the cable that was ordered was what they could find readily available overseas, is Turkish or Italian, and is rated for 70 deg C. Does this mean I can only derate from the 60 deg C column? Another piece to the puzzle is that the manufacturer's cutsheet for the cable shows that its ampacity ratings for 70 deg C are higher than the ampacities shown in the 90 deg C column in Table 310.16. Does this mean I can derate from the 90 deg C column, since the cables won't see the ampacities that will cause them to reach 70 deg C? Thanks.