Yes and no. Annex C conduit fill tables do not take into account short raceway nipples that are 24" or less because the permitted fill for those nipples is 60% instead of the standard 40% for more than two conductors. So when applying the tables if your raceway is more than 24" the number of conductors listed is the maximum permitted within the raceway. Raceway fill limits are to prevent the conductors from being damaged during installation. Derating has no bearing on the maximum fill. Derating is required when the number of CCC's exceeds three for raceways longer than 24". This may help when trying to figure out how many conductors are actual CCC's.Can you put more conductors in a conduit than the tables in Annex c allow and the derate? Or is that always a violation.
Here's some examples of when to count and not count the neutral as a current carrying conductor or CCC:
3Ø- 208Y/120 or 480Y/277 volt system-different circuit types:
A) 2 wire circuit w/ 1 ungrounded, 1 neutral = 2 CCC's
B) 3 wire circuit w/ 2 ungrounded, 1 neutral = 3 CCC's
C) 4 wire circuit w/ 3 ungrounded, 1 neutral = 3 CCC's*
Notes:
A) A normal 2 wire circuit has equal current flowing in each of the circuit conductors so they both count as CCC's.
B) In this circuit the neutral current will be nearly equal to the current in the ungrounded conductors so the neutral counts as a CCC
C) In this circuit the neutral will only carry the imbalance of the current between the three ungrounded conductors so it is not counted as a CCC, with an exception,
*if the current is more than 50% nonlinear (see below for NEC article 100 definition) then the neutral would count as a CCC.
1Ø- 120/240 volt system-different circuit types:
D) 2 wire circuit w/ 1 ungrounded, 1 neutral = 2 CCC's
E) 3 wire circuit w/ 2 ungrounded, 1 neutral = 2 CCC's
Notes:
D) A normal 2 wire circuit has equal current flowing in each of the circuit conductors so they both count as CCC's.
E) In this circuit the neutral will only carry the imbalance between the two ungrounded conductors so the neutral is not counted as a CCC.
Nonlinear Load. A load where the wave shape of the steady-state current does not follow the wave shape of the applied voltage.
Informational Note: Electronic equipment, electronic/electric-discharge lighting, adjustable-speed drive systems, and similar equipment may be nonlinear loads.
So when using all phases of a system in a circuit (at least in the provided systems) the neutral conductor only carries the unbalanced load making is a non CCC. (With exception of nonlinear loads.)Yes and no. Annex C conduit fill tables do not take into account short raceway nipples that are 24" or less because the permitted fill for those nipples is 60% instead of the standard 40% for more than two conductors. So when applying the tables if your raceway is more than 24" the number of conductors listed is the maximum permitted within the raceway. Raceway fill limits are to prevent the conductors from being damaged during installation. Derating has no bearing on the maximum fill. Derating is required when the number of CCC's exceeds three for raceways longer than 24". This may help when trying to figure out how many conductors are actual CCC's.
Any current in the neutral is current not being carried by one or more lines, so the total current can never exceed that which a fully-loaded balanced system would carry.Why on a theory level does the neutral function that way in those scenarios?
why do the 3 wire circuits on both systems differ on amount of CCC’s?Here's some examples of when to count and not count the neutral as a current carrying conductor or CCC:
3Ø- 208Y/120 or 480Y/277 volt system-different circuit types:
A) 2 wire circuit w/ 1 ungrounded, 1 neutral = 2 CCC's
B) 3 wire circuit w/ 2 ungrounded, 1 neutral = 3 CCC's
C) 4 wire circuit w/ 3 ungrounded, 1 neutral = 3 CCC's*
1Ø- 120/240 volt system-different circuit types:
D) 2 wire circuit w/ 1 ungrounded, 1 neutral = 2 CCC's
E) 3 wire circuit w/ 2 ungrounded, 1 neutral = 2 CCC's
Because the 3 wire circuit in the 3 phase system is unbalanced, but the 3 wire circuit in the single phase system is balanced.why do the 3 wire circuits on both systems differ on amount of CCC’s?
It has to do with the total resistive heat generated among the conductors.why do the 3 wire circuits on both systems differ on amount of CCC’s?
why do the 3 wire circuits on both systems differ on amount of CCC’s?
I’m realizing I’m not sure conceptually how current flows from phase to phase. I understand that it does, and that that is why no neutral is needed on 240 circuits. But I don’t know why. I know ac current oscillates back and forth at 60hz. But how current from one phase conductor to another as a return path without issue is something I haven’t thought through. I guess on an atomic level why not have electrons moving opposing ways? My brains thinks they’ll run into each other though.Another way to think about the neutral of 120/208 1ph:
With a balanced 3ph system, neutral carries no current. If you reduce the load on any one line, the neutral carries that much current. If you completely remove the load on any one line, the neutral carries all of that current.
A 20a, B 20a, C 20a, N 0a
A 20a, B 20a, C 15a, N 5a
A 20a, B 20a, C 10a, N 10a
A 20a, B 20a, C 5a, N 15a
A 20a, B 20a, C 0a, N 20a
At any instant in time, the two phase conductors are at opposite polarities. One is positive while the other is negative.I’m realizing I’m not sure conceptually how current flows from phase to phase. I understand that it does, and that that is why no neutral is needed on 240 circuits. But I don’t know why. I know ac current oscillates back and forth at 60hz. But how current from one phase conductor to another as a return path without issue is something I haven’t thought through. I guess on an atomic level why not have electrons moving opposing ways? My brains thinks they’ll run into each other though.
Even in three phase?At any instant in time, the two phase conductors are at opposite polarities. One is positive while the other is negative.
Kinda. Instead of being direct opposites, it more like one is more positive than the other.Even in three phase?
i see. That’s why there’s no four phase systems (at least that i know of). You’d have to be very careful when hooking up motors or equipment utilizing such a system, as if you are able to put the phases out of order. In three phase you can only have them reversed. Is that right?Kinda. Instead of being direct opposites, it more like one is more positive than the other.
Assuming balanced currents:Even in three phase?
i see. That’s why there’s no four phase systems (at least that i know of). You’d have to be very careful when hooking up motors or equipment utilizing such a system, as if you are able to put the phases out of order. In three phase you can only have them reversed. Is that right?
With 3ph, there is a genuine phase difference. The alternator has three sets of coils that are physically offset by (360/3) 120 degrees, so their outputs are electrically 120 degrees apart.Even in three phase?