It's because 120/240v 1ph is merely two 120v sources wired in series, just like two batteries, which must be wired in the correct polarity for the voltages to add, and not cancel.I’m realizing I’m not sure conceptually how current flows from phase to phase. I understand that it does, and that that is why no neutral is needed on 240 circuits. But I don’t know why.
When the POCO wires three 120/240v transformers for 240-Delta 3ph, they internally wire each unit's two 120v secondaries in series to obtain 240v from each one.
When they wire them for 208-Wye/120v 3ph, they internally wire each unit's two 120v secondaries in parallel to maintain the full capacity of each of the transformers.