I'm trying to figure why you are concerned about your existing service conductor ratings. Are you at any time going to be utilizing your existing service conductors for feeding power back to the utility as in an interactive PV system?The existing service is metered at the transformer, it has 8-sets underground landing in a two-section switchboard. The left section is a termination and pull section, the right section has up to 6 service disconnects sized 400A to 1200A each (there is no 3000A main existing). I would tap into that left section, and install a new section to the far left with a 3000A breaker for solar. Thats the 100% rated breaker we're talking about. The existing service conductors are the ones I am concerned about.
Does that clear it up?
Obviously, your existing service conductors are size to handle your existing load. Adding a PV inter-connection doesn't increase your load on the SE Lateral.
As long as your PV system has been sized properly and does not exceed the Buss rating of your switchboard, I don't see the effect on your existing SE.
Is your Switchboard rated at 100%? or just the Breaker?