Wire sizing for CNC machine

Status
Not open for further replies.

Deetz

Member
Location
MN
So we have a CNC coming in. It's 70kva at 220v. If I use a 112.5kva transformer do I need to size the primaries for the transformer or the load of the CNC after calculations and ratio changes?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
For your 112.5 kva transformer the primary conductors must have an ampacity no less than the primary overcurrent device.

Size your transformer
Select your overcurrnt device keeping 450.3 in mind
Select conductors based on the OCP device rating.
 