I have a piece of HVAC equipment with a Minimum circuit ampacity of 43 amps, and a Maximum Overcurrent protection of 60A. If I feed this unit directly from a 60A circuit breaker, I can use #8 wire (even though #8 is only rated for 50A). Right?
Here is the question: If I add a fusible disconnect at the equipment, can I still run #8 wire from the circuit breaker to the fusible disconnect? Or does this run change from a branch circuit to a feeder? If so, I would need #6 wire rated from 60A.
Thanks:
Steve