I agree with Dennis. #10 on 40A breaker.
Bzzt!
Wrong. It would have to be a 40A fuse. (Although you could certainly have it go through a breaker first.)
I agree with Dennis. #10 on 40A breaker.
Bzzt!
Wrong. It would have to be a 40A fuse. (Although you could certainly have it go through a breaker first.)
Photo reads Approved for HACR breakers or Time Delay Fuses.....
How about because it says "Maximum FUSE" but does not specify Maximum Breaker?Yes, and all breakers today are HACR rated per the standard. I'm thinking GoldDigger glossed over the HACR in the photo.
How about because it says "Maximum FUSE" but does not specify Maximum Breaker?
The peripheral mention of HACR breaker does not change the actual language elsewhere on the label.
OK, How about #10 with a 30 amp breaker?
OK, How about #10 with a 30 amp breaker?
That 30 would never work properly. It would trip all the time. Most inspectors wouldn't pass it either
Are you sure? The MCA already has a 125% factor added to it so the running current is probably less then 25 amps and an inverse time CB should allow the unit to start. Not saying I would do it but a 30 amp OCPD would be code compliant.
PHP:
Going by experience , even a 5 amp reduction will cause nuisance trips.
Sounds like a nuisance to me.I had a 30 kva three phase 208-600 transformer (83 amps at 208) on a 60 amp breaker and it would trip on energizing about 1 out of 5 or 6 times.
Sounds like a nuisance to me.![]()
PHP:
That 30 would never work properly. It would trip all the time. Most inspectors wouldn't pass it either