Wire sizing

Brandon002

Member
Location
Tennessee
Occupation
I want to be an electrician
Ok so if there was a question
( size a THHN for a 49a load terminating to a 75c terminal)
You would still stay and size your wire in that column right?


Sent from my iPhone using Tapatalk
 
Ok so if there was a question
( size a THHN for a 49a load terminating to a 75c terminal)
You would still stay and size your wire in that column right?
Assuming a non-continuous load, which would allow you to use a 50A breaker, and 75C sizing on both ends, you'd be correct. There is a burden of proof to use 75C ratings on both ends for 100A and less, but most commonly, modern equipment will meet this burden of proof.

#8 Cu would limit you to a 50A breaker in this context.
 
So I’ve had a hard time fully understanding which column to go by and when.. from my understanding the 60degree column is always for romes? 75 degree column would be for 100a or less, and 90 degree is for over 100a and adjustment factors?
 
So I’ve had a hard time fully understanding which column to go by and when.. from my understanding the 60degree column is always for romes? 75 degree column would be for 100a or less, and 90 degree is for over 100a and adjustment factors?
Romex (i.e. NM cable) is a special case, where you're limited to the 60 C column for terminations, regardless of conductor or terminal ratings. SE cable is governed by a similar rule, when routed in thermal insulation.

#10Cu and less, you have the small conductor rule.
100A and less, there is a rule that is more academic than practical, which is that 60C is the default. You have a burden of proof to show that terminations on both ends can handle anything higher. Most modern equiment meets this burden of proof, so 75C most commonly governs terminations.
Anything over 100A, and 75C is the default.

In all of the above cases, you can use a higher rating that comes with the wire type, as the starting point for derate calculations, which is the primary value in 90C rated wire, despite a 75C terminal limitation.
 
Ok so if there was a question
( size a THHN for a 49a load terminating to a 75c terminal)
You would still stay and size your wire in that column right?


Sent from my iPhone using Tapatalk
Often (usually? aways? Wish I really knew...) a conductor is rated at 125% of the load. For example:

2020 NFPA 424.4(B) BranchCircuit Sizing. The brand-circuit conductors for fixed electric space-heating equipment and any associated motors shall be sized not smaller than 125 percent of the load.

So in this case I would say the answer would be #6 copper AWG

49 amps x 1.25 = 61.25 amps
 