must be the same guy using the welding cable
Unsure what type of voltage motoe you are delaing with, if it's a 480 volt 3 phase motor then:
will it work ? probably, just like the welding cable will work.
does it meet NEC ? probably not... but more info would be in order.
ass-u-ming a 335 hp (this time you stated HP) motor would have a FLA of about 400 amps requiring 500 amp comductors. Parrell 3/0s in seperate conduits under normal ambient would be 400 amps.
However, 4/0cu is only good for 230amp. I see it as upsizing to 2 sets of 250kcm.the contractor on a job where I work is running 2 sets parelled 4-0 3phase 480 v
runs to a 500 amp breaker
After the last two topics you posted, I get the feeling you are wanting someone to design the projects, if I am wrong, I apologize.
I would refer you to Art 430 on motors, and 310 on amapcities.
In your previous post I indcated the steps for sizing motor conductirs.
You indicate 10 years contractor experience so those sections should not be foreign.
You tell us how you would wire it, and how you obtained that and I will be glad to provide my opinion.
Someone else may approach differently.
(Mr. Moderator, if I overstepped my bounds I apologize.)