Similar to the EGC sizing question.
I have a VFD with 232A FLC input. The VFD manufacturer says I can go as high as a 700A CB to feed it.
For whatever reason I select a 700A CB.
Am I trapped into sizing the input conductors so they are protected by a 700A CB?
(2) 1/0 wires per phase [125% of 232 is just under 300A - the ampacity of (2) 1/0 wires] is a whole lot nicer then (2) 500 MCM wires per phase.