J jbolen Senior Member Nov 23, 2008 #1 In Iraq needing ....Table of Ampacities for metric wire. m/m .4 .5 1.0 1.5
celtic Senior Member Location NJ Nov 23, 2008 #2 Starting at Table 5 in Chapter 9 in the NEC [way in the back] has the numbers you need
Smart $ Esteemed Member Location Ohio Nov 23, 2008 #3 jbolen said: In Iraq needing ....Table of Ampacities for metric wire. m/m .4 .5 1.0 1.5 Click to expand... 0.4 mm ~ 18 AWG (0.39 mm) 0.5 mm ~ 16 AWG (0.49 mm) 1.0 mm ~ 10 AWG (0.98 mm) 1.5 mm ~ 6 AWG (1.56 mm)
celtic Senior Member Location NJ Nov 23, 2008 #4 celtic said: Starting at Table 5 in Chapter 9 in the NEC [way in the back] has the numbers you need Click to expand... jbolen said: In Iraq needing ....Table of Ampacities for metric wire. Click to expand... Upon further review of your question, it would seem you need Table 5 as well as Table 310.16. Your ampacity will vary with insulation type.