jumper
Senior Member
- Location
- 3 Hr 2 Min from Winged Horses
Nice solution Bes, I like it.:thumbsup:
Bending space would be a limiting factor to what NEC would let you install, will not change what size lugs are in the breaker used.
The lugs will depend on what breaker is used, there is more then one 400 amp breaker. Just some fairly common examples from the catalog would include the LA/LH series with lugs accepting 1 -600 or 2 - 250's or the LC/LI (which is a 600 amp frame) accepts 2 -500's
At the bottom of the chart is a note telling you to go to a different page for optional lugs, which unfortunately I think sent me to wrong page, but I believe it is sending you to same options as there is for the general use L series breakers you just have the plug on bus end for I line that is not changeable the other end is same as other L series - or for within any other series for that matter.
Infinity never seen those. Is that something new. I'm going to ask my supply house about them. Could of used them a few times.