Working on a project where the plans call out a 8AWG conductor, however the CB can accept up to a 10AWG conductor. The oversized wire must be for voltage drop. Is it acceptable to splice a short piece of 10AWG(1'-2') to the 8AWG conductor in the panelboard so that it can be terminated to the CB? The other suggestion I'd suggest to the engineer is to replace existing CB with a larger frame.
Thanks.
RC