mdshunk said:
I must have a bum copy of the code. It doesn't say that at all in mine.
Think about a detached garage, pole barn, etc... then take a look at 334.10 under uses permitted.
(1)One- and two-family dwellings.
Is this one or two family dwelling? Take a look at definition of such.
Dwelling, One-Family. A building that consists solely of one
dwelling unit.
Dwelling, Two-Family. A building that consists solely of two
dwelling units.
Dwelling Unit. A single unit, providing complete and independent living facilities for one or more persons, including permanent provisions for living, sleeping, cooking, and sanitation.
Is this a dwelling? No....Then look at 334.10(2)Multifamily dwellings permitted to be of Types III, IV, and V construction except as prohibited in 334.12.
It wasn't a one or two, It definitely isn't a multi...
So that leaves us with 334.10(3)
(3)Other structures permitted to be of Types III, IV, and V construction except as prohibited in 334.12. Cables shall be concealed within walls, floors, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies.
It must be an "other"... One that if I put NM in it, it must be concealed behind that 15 min finish....
Jim
New Hampshire